Hi there. Question: What would the required framing stud size be for external walls in a new building in NYC that is 5 stories high? Is it 2×4 or 2×6? Thanks much for your help.


Comments

  1. A number of issues here, biggest one being that you’re building with wood, forget about the size for now. Wood stud construction, new code = Type 3 or Type 5 construction class. Type 5 is not allowed within the fire district, which is all of Brooklyn. Type 3 cannot be used for residential construction of more than one or two families, and is further limited to 3 stories if no sprinkler system.

  2. What are you building that is 5 stories tall out of wood studs? You will find that to meet the energy code will require a thicker stud than needed structurally unless you are going to use spray foam for the insulation.